One of my motors is set up to a mini capstan kind of like this (link) that moves a trolley along a rail. So the load is just a friction load, albeit a fairly high amount of friction.
The problem I’m having is that the calibration doesn’t seem to have enough force to be able to run any of the calibration sequences. I’ve bumped up the calibration current up to 25 amps but when I looked at the graph during various calibration sequences it doesn’t even get close to that high (the highest amps I saw was about 7 or 8). I also tried bumping up the odrv0.axis1.motor.config.resistance_calib_max_voltage which didn’t seem to help either.
The error that appears after trying the full calibration sequence is:
system: no error
axis: no error
motor: no error
axis1
axis: no error
motor: Error(s):
MOTOR_ERROR_PHASE_INDUCTANCE_OUT_OF_RANGE
MOTOR_ERROR_CURRENT_LIMIT_VIOLATION
Oddly enough I manually pushed the motor to the point where the index is, then ran the odrv0.axis1.requested_state = AXIS_STATE_ENCODER_INDEX_SEARCH
and this made the full calibration sequence work properly and allowed me to go into closed loop control and move around.
Obviously that’s not a real solution so I’m scratching my head to figure out what else to try.
Thanks for your help!
Im interested to learn how you solved the problem. Im to having similar aplication with a lot of friction, and the motor cannot calibrate it self properly.
Just to clarify: I see that you have motor.config.pre_calibrated = True, you did successfully run either MOTOR_CALIBRATION or FULL_CALIBRATION_SEQUENCE before setting this value and then saved the configuration? These errors suggest that the motor calibration did not run successfully or was not saved.
Are you able to get the ODrive and motor fully calibrated and running closed loop control with the high friction load removed?
I hadn’t actually successfully run those before saving the calibration config, good point. I’ll try this without and report back. Thanks for noticing that.
I had a similar situation and issue. I was able to resolve it by increasing calibration_lockin.current and general_lockin.currrent (I think the default is 10 amps).
Then at reboot you just do the index search (not the offset calibration) and you should be good. If you need more torque then increase the calibration and general lockin currents as suggested by trumans24.
The motor was under a decent friction load. I removed the load.
rebooted the system.
started going through the setup proceedure that has worked with axis0 on this odrive (axis0 performs a different function).
checked the lockin currents. considering there is no more load, they seem high.
rebooted
checked the current values were still set
tried running index search and it failed
cleared errors
tried running full calibration sequence and it failed again.
completely lost
In [3]: odrv0.axis1.motor.config.pre_calibrated = False
In [4]: odrv0.save_configuration()
Oh no odrv0 disappeared
Reconnected to ODrive 206235A55748 as odrv0
In [5]: odrv0.axis1.config.general_lockin.current
Out[5]: 10.0
In [6]: odrv0.axis1.config.calibration_lockin.current
Out[6]: 10.0
In [7]: odrv0.reboot()
In [8]: odrv0.axis1.config.calibration_lockin.current
Out[8]: 10.0
In [9]: odrv0.axis1.requested_state = AXIS_STATE_ENCODER_INDEX_SEARCH
In [10]: dump_errors(odrv0)
system: no error
axis: no error
motor: no error
axis1
axis: no error
motor: Error(s):
MOTOR_ERROR_MODULATION_IS_NAN
In [11]: odrv0.clear_errors()
In [12]: odrv0.axis1.requested_state = AXIS_STATE_FULL_CALIBRATION_SEQUENCE
In [13]: dump_errors(odrv0)
system: no error
axis: no error
motor: no error
axis1
axis: no error
motor: Error(s):
they are set at 10 A. The system has no resistance. 10A can move a couple lbs. This should be more than enough. I could try increasing it still, but I’d be surprised if it helped so i didn’t try it yesterday
Out[5]: 10.0
Out[6]: 10.0
This means the motor didn’t calibrate properly. Can you paste your whole procedure? Just the commands you’re sending in a blob. If the motor and encoder are physically working correctly, this is all you should need:
You can plot the current consumption during closed loop(which you can start manually, as you described above) and see what current does your motor need to move in closed loop. Then you can set the locking currents high enough so the motor can overcome the load while calibrating. That is what i have done and it worked for me.
it works now! I thought my motor was broken. the erase_configuration() was the key for sure.
The odrv0.axis1.config.general_lockin.current and odrv0.axis1.config.calibration_lockin.current might come in handy when I add the friction back on, but for now its nice to know it moves.
Problem not fully solved, but subproblem solved. will update once I try again with friction load.
i tried again and it failed. friction is still off the system and i ran the following
In [6]: odrv0.erase_configuration()
In [7]: odrv0.config.enable_brake_resistor = True
In [8]: odrv0.config.dc_max_negative_current = -1
In [9]: odrv0.axis1.encoder.config.use_index = True
system: no error
axis: no error
motor: no error
axis1
axis: no error
motor: no error
In [11]: odrv0.axis1.requested_state = AXIS_STATE_FULL_CALIBRATION_SEQUENCE
In [12]: dump_errors(odrv0)
system: no error
axis: no error
motor: no error
axis1
axis: no error
motor: Error(s):
MOTOR_ERROR_BRAKE_RESISTOR_DISARMED
is there another company you would recommend that has a more straightforward process of turn on, set amp limit, move motor. Its been days if not weeks of messing around with the tutorials/setups/these threads
Kollmorgen, Yaskawa, Siemens, Parker. The idea with ODrive is to make motor control more accessible… but there are growing pains. We recognize that the user experience could be better, but I don’t think 6 configuration commands is particularly egregious
any idea why this one variable isn’t saving. the second disappearing is when I power off the system after the configuration.
In [86]: odrv0.axis1.motor.config.current_lim
Out[86]: 12.0
In [87]: odrv0.axis1.motor.config.current_lim = 20
In [88]: odrv0.clear_errors()
In [89]: odrv0.save_configuration()
In [90]: odrv0.axis1.motor.config.current_lim
Out[90]: 12.0
Thanks for noticing the brake resistor had come out and wasn’t plugged in.
The following sequence of events has been working. I’m confused why the one configuration param needs to be reset after every time the system is turned off and on, but its a bug we can work with.
That generally means you’re having USB noise issues, but since it’s just this one parameter I’m inclined to believe maybe it’s some other device setting the current_lim. Because the default is 10, not 12… So that’s strange.
SOLVED